Radian 8048 Shuts off on surge

Dual Input, 120/240, stainless steel form factor design for unsurpassed surge capability
Post Reply
fredb
Forum Junior Member
Posts: 1
Joined: Mon Sep 26, 2016 11:08 am

Radian 8048 Shuts off on surge

Post by fredb » Tue Oct 18, 2016 12:20 pm

I have recently purchased a Radian GS8048A.
It works great until I have a surge load, such as the refrigerator or vacuum turning on. Then the inverter shuts off.
I know I am not going over the Wattage. My previous inverter had a surge of 5k and I never had any issues.
I have contacted the Outback dealer I purchased it from and they had no explanation.
I do not have a Mate yet. I have been told the inverter will run in a default mode with out it.
I am off grid and use only solar for power.

Has anyone experienced this with this inverter?

petertearai
Forum Guru
Posts: 397
Joined: Fri Aug 06, 2010 4:35 pm
My RE system: 2220 watt pv, fm80, outback fxr 2000 watt inverter. Shoto 12 times 2 volt exc400 lead carbon batterys 24 volt system victron battery moniter. optics RE
Location: NewZealand North Island

Re: Radian 8048 Shuts off on surge

Post by petertearai » Tue Oct 18, 2016 11:55 pm

hi . I dont have a radian . But the only suggestion i have would be the voltage is dropping to the low voltage shut off. maybe watch the voltage on vacume start up .
2220 pv. fm80. 12 times 2 volt exc shoto lead carbon 450 AH 24 volts. victron battery monitor. outback fxr 2000 watt inverter

Vic
Forum Czar
Posts: 995
Joined: Sun Jul 09, 2006 12:56 pm
Location: San Joajuin County, CA

Re: Radian 8048 Shuts off on surge

Post by Vic » Wed Oct 19, 2016 6:34 am

Hi fredb, Welcome to the Forum.

We do know almost nothing of your system. What type and model number are your batteries?
Do you have multiple strings of batteries? What number of strings of batteries are on the system?
What is the Ah Capacity of the battery bank?

What is the total power of your solar array?
Assume that you are using Outback FM Charge Controllers (CC), which one/s and what number of CCs are on the system?

I have not looked at the Defaults for Absorb voltage, Absorb time, and Float voltage on the Radians, but, in general these Defaults are very cautious, and almost always need to be changed to fully-charge batteries.

Agree with peter, that it is most likely that the inverter is reaching Low Voltage Disconnect, and it is most likely that this is due to low State Of Charge (SOC) of the batteries.

Perhaps, this could also be from very cloudy conditions, or generally, loads that exceed the Solar power available.

There will be more questions, but some more data will help the conversation.

You probably DO need a Mate, even a borrowed one for now. As the Default charge settings will probably need to be changed.

Thanks for some more answers. Vic
4/20/08: 18 Shell SQ 175-106 Vmpp, Stacked 5548 SW+, 1350 AH Surrette 4KS25's, MX-60, Kubota SQ-3250 25 KVA Polyphase Diesel genset. Thanks OutBack for this Forum + the great Support and Service.

EMCF
Forum Virtuoso
Posts: 93
Joined: Thu Jul 21, 2016 10:22 am
My RE system: FX3048, 4 200a batteries, FM60. 3 kw array

Re: Radian 8048 Shuts off on surge

Post by EMCF » Wed Oct 19, 2016 2:31 pm

The size of cables that go from battery bank to Radian can be a factor too. Make sure they are of adequate size.
Outback Fanboy at your service

SwDoctor
Forum Member
Posts: 17
Joined: Fri Aug 04, 2017 6:24 pm
My RE system: Radian, Mate3, FlexNet, FlexMax

Re: Radian 8048 Shuts off on surge

Post by SwDoctor » Tue Jul 02, 2019 1:33 pm

6years so far on that inverter off grid solar only.
No issues.

But: i think your problem will be a bad battery or bad connection to the battery.
whereas the voltage drops enough to kick off the inverter when a load is present.
Mate3 would reveal this, but you can test for it by using a varying load, for example- start with a 100w load then measure the batteries, step up to a 300w load, repeat, etc.
If your battery (or cable) is faulted you will see it drop in voltage far more than it should.

Your batteries could be okay, and just be too "small" for the application. (not enough "amp hours")

My unit is operating with THREE forklift batteries (680ah each - x3!), and since I am heavy into automation I have engineered a triple "centerpoint" monitor that literally watches the midpoint of each battery in respect to the midpoints of each other battery, and anything other than zero volts indicates an imbalance, of course with allowances for aging and cable differences, the automation PC can predict battery faults LONG before one can be "felt" in real live operation. So far has triggered twice, replaced the two bad cells and no problems since. The automation PC also keeps up with AH in/out and waters the batteries automatically. It's like living on grid without any bills!

If your battery tests good, you may also consider that if your vacuum cleaner (for example) is the only load that triggers it, then it could be the faulty (shorted) cause.

Post Reply