SOC doesn't change on a SE-830PLR-300

Discussion about the OutBack OpticsRE system monitor

Moderators: OutBack Moderator Team, OutBack

Post Reply
ECI_Solar
Forum Junior Member
Posts: 1
Joined: Wed Sep 16, 2020 1:30 pm

SOC doesn't change on a SE-830PLR-300

Post by ECI_Solar » Wed Sep 16, 2020 1:46 pm

We recently completed an install of a SE-830PLR-300 system and once we got the OpticsRE functioning (bad Mate3S), the SOC never changes from 87%, however battery voltage and temperature track fine. I am having a difficult time determining how to reset the SOC so that it will track. Is it possible to do through the settings in OpticsRE?

Thanks,

fcwlp
Forum Czar
Posts: 527
Joined: Wed Jan 22, 2020 9:40 am
My RE system: GS8048A, FM80 w/3,600 W PV Fixed, FM80 w/2,700W on Zomeworks tracker, Mate3, 24 Trojan 2V L16 1100AH @ C20, Grid-Tied with Kohler 14RESA LPG Generator and MEP-803 Diesel if needed
I also install and maintain grid-tied and off-grid systems, details will be given for these system if required
Location: 80 miles NE of Phoenix at 5500'

Re: SOC doesn't change on a SE-830PLR-300

Post by fcwlp » Fri Sep 18, 2020 9:25 am

Unplugging and replugging the FNDC cable will reset the SOC to 100%. However, my guess is you have something wrong with the settings in the FNDC, the shunts are not wired correctly, or the shunts are not enabled in the FNDC.