GS8048 + Lithium + LBCO

Post by PaulMillner » Tue Sep 15, 2020 7:35 pm

Howdy,

Wanted to share an aha... my GS8048A came with firmware 1.5.4, April 2017 dated. Not sure why... it's less than a year old.

I'm running the Samsung ESS batteries, 16 lithium cells, battery range 49.6 to 65.6 volts. But 1.5.4 doesn't allow a battery disconnect voltage above 48 volts... a tenth of a volt per cell below minimum, assuming perfect balancing... that's battery damage territory.

Reading the release notes on the various firmware versions that have come since, it's not apparent that the LBCO, low battery cut out, got changed... but updating to 1.6.7, the LBCO maximum did improve... and I've set mine to 51.2 giving each cell an extra tenth of a volt wiggle room. :-)

Anyway, a report on a favorable outcome.

Paul

PS: What does the GS in GS8048A stand for, at least allegorically?

raysun
Forum Emperor
Posts: 2962
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: GS8048 + Lithium + LBCO

Post by raysun » Wed Sep 16, 2020 12:20 am