Wizard settings for Gen Upper Voltage Limit

Mate3 and Mate3s communications devices for Outback Power

Wizard settings for Gen Upper Voltage Limit

Postby whansteen on Fri Nov 10, 2017 1:47 pm

Hi,

I'm programming the Mate3, and I need help with the correct settings for Gen Lower Voltage Limit and Gen Upper Voltage Limit. I have a Generac Guardian 8kW 120/240 and the tech support for my generator had no idea. Any idea what the upper and lower voltage limit settings should be?

Thanks!
whansteen
Member
 
Posts: 7
Joined: Wed Oct 25, 2017 1:55 pm
My RE system: Outback FPR-4048A Pre-Wired System
Generac Guardian 8kW Generator
24 Trojan L16RE-2V 2V 1110 AH Batteries

Re: Wizard settings for Gen Upper Voltage Limit

Postby Mike Curran on Sat Nov 11, 2017 10:35 am

I think these settings are more for you to limit what your inverter will accept than for matching your generator's limits. These are the same voltages your house wiring and loads may see when the generator is running so you want to set them accordingly. Don't want to burn up any expensive electronics! :eek:
Mike Curran
OutBack Guru
 
Posts: 334
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback: 8 (2x4) Evergreen 180's into one MX60, 6 (2×3) ALEO S79-300's into one FM80, 2 grid-tied GVFX3524's classic stacked for 120/240VAC, 12 Surrette/Rolls 2V x 1766Ah, Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar: 30 (2x15) 235W panels with Enphase M215 microinverters. 6,450 nameplate watts AC, grid-tied.

Re: Wizard settings for Gen Upper Voltage Limit

Postby blackswan555 on Sat Nov 11, 2017 8:21 pm

I think these settings are more for you to limit what your inverter will accept than for matching your generator's limits
You think correctly :grin: Its the high and low the inverters will drop the gen, I am not sure of the defaults on your inverter ? but all the rest, Default is fine,

Tim
My comments are based on my experience and research, They are not endorsed or checked by Outback.I am an independent British electrician living in Spain, So please take this into account when reading /acting on my post`s.
blackswan555
OutBack Emperor
 
Posts: 2516
Joined: Sat Aug 30, 2008 5:50 am
Location: Ibiza Spain,
My RE system: Other peoples, VFX "E" versions, FLA`s, Generators.

Re: Wizard settings for Gen Upper Voltage Limit

Postby whansteen on Sat Nov 11, 2017 8:26 pm

Thanks!
whansteen
Member
 
Posts: 7
Joined: Wed Oct 25, 2017 1:55 pm
My RE system: Outback FPR-4048A Pre-Wired System
Generac Guardian 8kW Generator
24 Trojan L16RE-2V 2V 1110 AH Batteries


Return to Mate3 / Mate3s