Outback Flexmax 80 goes from Bulk to float

Post by Cucuback » Thu May 16, 2019 3:25 pm

Hi guys i have an issue with my FM 80 , the controller jumps from bulk to float , no absorption time at normal charge cycles.

Mike Curran
Forum Emperor
Posts: 1385
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied, no longer AC- coupled

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W (DC array input to SB charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 modules

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Outback Flexmax 80 goes from Bulk to float

Post by Mike Curran » Thu May 16, 2019 6:52 pm

What other equipment do you have in your system? Are you off grid or grid-tied? What do you mean by "at normal charge cycles"?

If you fill in your system profile it will make it easier for the forum to help you.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

Cucuback
Forum Member
Posts: 11
Joined: Mon Jun 25, 2018 5:02 pm
My RE system: Flexmax 80, Schneider Sw 4024 inverter , 6 Solar World 340XL Mono, 4 Deka 370ah batts .
Location: PR US.

Re: Outback Flexmax 80 goes from Bulk to float

Post by Cucuback » Fri May 17, 2019 2:18 am

9 Solar World 300 watts mono panels
1 FM 80
1 6k Sigineer inverter 48vdc
16 Alpha Cell 114ah 12v Agm Batt

Normal charge cycles means (not equalizing)
I know 3 other guys the FM 80 do it the same problem.
Temperature these days are in the 90-92┬░ F range.

Cucuback
Forum Member
Posts: 11
Joined: Mon Jun 25, 2018 5:02 pm
My RE system: Flexmax 80, Schneider Sw 4024 inverter , 6 Solar World 340XL Mono, 4 Deka 370ah batts .
Location: PR US.

Re: Outback Flexmax 80 goes from Bulk to float

Post by Cucuback » Fri May 17, 2019 4:13 am

Off grid.

raysun
Forum Emperor
Posts: 1651
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Outback Flexmax 80 goes from Bulk to float

Post by raysun » Fri May 17, 2019 4:22 am

Are the panels wired as 3 series strings?

The battery is 4 series strings of monoblocks, correct?

How many sun hours does your location average daily?

On the FM80 what are the following settings values:
Absorb voltage
Absorb time
Absorb end Amps

Cucuback
Forum Member
Posts: 11
Joined: Mon Jun 25, 2018 5:02 pm
My RE system: Flexmax 80, Schneider Sw 4024 inverter , 6 Solar World 340XL Mono, 4 Deka 370ah batts .
Location: PR US.

Re: Outback Flexmax 80 goes from Bulk to float

Post by Cucuback » Fri May 17, 2019 9:03 am

Absorb 57.6
Absorb time 4.0 hrs
Absorb end amp 4 amps
Panels in strings of 3
Batteries 4 sets of 4 parralel

Cucuback
Forum Member
Posts: 11
Joined: Mon Jun 25, 2018 5:02 pm
My RE system: Flexmax 80, Schneider Sw 4024 inverter , 6 Solar World 340XL Mono, 4 Deka 370ah batts .
Location: PR US.

Re: Outback Flexmax 80 goes from Bulk to float

Post by Cucuback » Fri May 17, 2019 9:04 am

5.5 hours of sun average.

raysun
Forum Emperor
Posts: 1651
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Outback Flexmax 80 goes from Bulk to float

Post by raysun » Fri May 17, 2019 9:06 am

Try setting the Absorb End Amps to 0 (zero).

Mike Curran
Forum Emperor
Posts: 1385
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied, no longer AC- coupled

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W (DC array input to SB charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 modules

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Outback Flexmax 80 goes from Bulk to float

Post by Mike Curran » Sun May 19, 2019 9:11 am

Cucuback wrote:9 Solar World 300 watts mono panels
1 FM 80
1 6k Sigineer inverter 48vdc
16 Alpha Cell 114ah 12v Agm Batt
I'm confused. Your profile says "My RE system: Flexmax 80, Schneider Sw 4024 inverter , 6 Solar World 340XL Mono, 4 Deka 370ah batts".
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

Cucuback
Forum Member
Posts: 11
Joined: Mon Jun 25, 2018 5:02 pm
My RE system: Flexmax 80, Schneider Sw 4024 inverter , 6 Solar World 340XL Mono, 4 Deka 370ah batts .
Location: PR US.

Re: Outback Flexmax 80 goes from Bulk to float

Post by Cucuback » Sun May 19, 2019 12:12 pm

The Schneider system is my home, the Sigineer is my neighbor house.

Mike Curran
Forum Emperor
Posts: 1385
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one MX60 (2007)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied, no longer AC- coupled

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W (DC array input to SB charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input from 14 Talesun 275W, Enphase M215 modules

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: Outback Flexmax 80 goes from Bulk to float

Post by Mike Curran » Mon May 20, 2019 5:46 pm

I'm trying to understand how you've determined that there's no absorb stage occurring. Are you watching the FM80'S LCD display when it jumps from bulk to float? If not, what leads you to believe there's no absorb?

With the settings that you have, I can't think of a reason that your system doesn't have an absorb period. Even if you reset end amps to zero as Raysun suggests, the end amps setting comes into play only after absorb voltage has been reached.

This is a shot in the dark, but make sure the absorb voltage setting on your FM80 is at least 0.2 volts higher than the setting on your Schneider inverter.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

Cucuback
Forum Member
Posts: 11
Joined: Mon Jun 25, 2018 5:02 pm
My RE system: Flexmax 80, Schneider Sw 4024 inverter , 6 Solar World 340XL Mono, 4 Deka 370ah batts .
Location: PR US.

Re: Outback Flexmax 80 goes from Bulk to float

Post by Cucuback » Tue May 21, 2019 5:26 am

Thanks for the reply, in the day history Absorb time =0
Float time 7.46, OFF Grid , inverter charger not enable , this happens another 3 guys i knew. These days are very hot here.

User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: Outback Flexmax 80 goes from Bulk to float

Post by Kurt Lundquist » Tue May 21, 2019 7:19 am

Does the battery bank drop below 49.6V at night? The controller does not add Absorb time unless the battery voltage gets low enough per this chart:
FM_Absorb_Timer.PNG
See pages 20-21 of the manual for more details http://www.outbackpower.com/downloads/d ... manual.pdf

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/

raysun
Forum Emperor
Posts: 1651
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Outback Flexmax 80 goes from Bulk to float

Post by raysun » Tue May 21, 2019 8:17 am

Kurt Lundquist wrote:Does the battery bank drop below 49.6V at night? The controller does not add Absorb time unless the battery voltage gets low enough per this chart:
FM_Absorb_Timer.PNG
See pages 20-21 of the manual for more details http://www.outbackpower.com/downloads/d ... manual.pdf

-Kurt
Kurt,

Are you saying that if the battery never drops below 49.6V, the charger will never enter the Absorb cycle?

User avatar
Kurt Lundquist
Alpha Energy Engineering
Posts: 1447
Joined: Tue May 31, 2011 7:23 am
My RE system: VFX3524, Mate3, 200Ah 24V AGM Battery Bank
Location: Arlington, WA

Re: Outback Flexmax 80 goes from Bulk to float

Post by Kurt Lundquist » Tue May 21, 2019 10:00 am

raysun wrote:Are you saying that if the battery never drops below 49.6V, the charger will never enter the Absorb cycle?
The answer is yes and no. The first time the controller is turned on and programmed the charge timer (ChgT in the MISC Menu) will be 0000. Once the battery voltage is at or above Absorb the ChgT will count up minutes until it meets your programmed Absorb time. If you have 4 hrs Absorb programmed the ChgT will count up to 0240 (240 minutes) then exit the Absorb cycle assuming there is enough sunlight/power. If the battery bank does not drop below 49.6V the next day the ChgT will still be 0240. If the ChgT is full then the system does not need to spend time in Absorb.

So the short answer is the FM will Absorb to your programmed time the first time you run it, then it will only Absorb as much as it thinks it needs to based off the chart I posted earlier.

Keep an eye on the ChgT in the MISC Menu for Absorb time details. While in the MISC menu if you press NEXT then BULK the ChgT will reset to 0000 and the controller will start a new Bulk/Absorb cycle.

Hope this helps.

-Kurt
Kurt Lundquist
Renewable Energy Project Engineer
http://alphaenergy.us/

raysun
Forum Emperor
Posts: 1651
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Outback Flexmax 80 goes from Bulk to float

Post by raysun » Tue May 21, 2019 11:23 am

Kurt Lundquist wrote:
raysun wrote:Are you saying that if the battery never drops below 49.6V, the charger will never enter the Absorb cycle?
The answer is yes and no. The first time the controller is turned on and programmed the charge timer (ChgT in the MISC Menu) will be 0000. Once the battery voltage is at or above Absorb the ChgT will count up minutes until it meets your programmed Absorb time. If you have 4 hrs Absorb programmed the ChgT will count up to 0240 (240 minutes) then exit the Absorb cycle assuming there is enough sunlight/power. If the battery bank does not drop below 49.6V the next day the ChgT will still be 0240. If the ChgT is full then the system does not need to spend time in Absorb.

So the short answer is the FM will Absorb to your programmed time the first time you run it, then it will only Absorb as much as it thinks it needs to based off the chart I posted earlier.

Keep an eye on the ChgT in the MISC Menu for Absorb time details. While in the MISC menu if you press NEXT then BULK the ChgT will reset to 0000 and the controller will start a new Bulk/Absorb cycle.

Hope this helps.

-Kurt
Kurt,

That quite succinctly describes a good bit of the behavior, myself, and I think others, have been scratching our heads over.

It would be great if this exact info found it's way into a sticky post in the FlexMax forum.

Cucuback
Forum Member
Posts: 11
Joined: Mon Jun 25, 2018 5:02 pm
My RE system: Flexmax 80, Schneider Sw 4024 inverter , 6 Solar World 340XL Mono, 4 Deka 370ah batts .
Location: PR US.

Re: Outback Flexmax 80 goes from Bulk to float

Post by Cucuback » Tue May 21, 2019 3:01 pm

The bank never go below 50.0 vdc, thanks for answering.

raysun
Forum Emperor
Posts: 1651
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, (2) FM80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: Outback Flexmax 80 goes from Bulk to float

Post by raysun » Tue May 21, 2019 8:00 pm

Cucuback wrote:Thanks for the reply, in the day history Absorb time =0
Float time 7.46, OFF Grid , inverter charger not enable , this happens another 3 guys i knew. These days are very hot here.
So now you can tell the other three guys what's happening!