Efficiency of MX60 for 24v to 12v conversion

Postby JPF on Tue Nov 29, 2005 11:49 am

JPF
Forum Junior Member
 
Posts: 2
Joined: Tue Nov 29, 2005 10:56 am
Location: Bellingham, WA

Postby Kent Osterberg on Wed Nov 30, 2005 4:03 am

The efficiency curves in the MX-60 manual suggest that the MX60 efficiency only drops about 1% if you wire the PV array in a 24-volt configuration rather than a 12-volt configuration. The improvement in wire losses between the PV array and the MX60 can easily make that up.

The system that you are proposing operates the MX-60 on the low end were it's effiency is the poorest. Still, the efficiency should be about 95% when in full sunlight.

For such a small system, the MX60 may not be the most economical choice. The price for a Sharp 123 is about the same as the price of a MX-60. Compare option A: two Sharp 123 modules and a MX60 and option B: three Sharp 123 modules and a brand X charge controller. Cost of the two options is similar but you'll get more charging current from option B.
Kent Osterberg
Forum Emperor
 
Posts: 1514
Joined: Mon Jun 09, 2003 11:01 pm
Location: Cove, Oregon
My RE system:

Postby JPF on Wed Nov 30, 2005 5:16 am

Thank you for the response.

Option A is actually two higher wattage panels such as the Sharp 208's which have a nominal voltage of 24 volts. So, from what I understand, I would need a charge controller like the MX60 to reduce that voltage to charge my 12 v battery setup. Given that I am trying to maximize wattage in a small space and that loss in efficiency is only 1% for voltage reduction it seems like this is the way to go.

Would wiring the two Sharp 208's together for 48 volts improve the performance of the mx60?

Thanks again
JPF
Forum Junior Member
 
Posts: 2
Joined: Tue Nov 29, 2005 10:56 am
Location: Bellingham, WA

Postby Kent Osterberg on Wed Nov 30, 2005 8:53 am

Kent Osterberg
Forum Emperor
 
Posts: 1514
Joined: Mon Jun 09, 2003 11:01 pm
Location: Cove, Oregon
My RE system:

Postby crewzer on Wed Nov 30, 2005 9:44 am

090805 System Configuration: 966 W STC (849 W CEC PTC) 48V PV array, FM80, 24V x 400 Ah AGM battery bank, FX2524T w/ BTS, Hub-4 & Mate; Link-10 w/ BTS, & E-Panel.
User avatar
crewzer
Forum Emperor
 
Posts: 1927
Joined: Mon Sep 27, 2004 10:50 am
Location: Vienna, VA

Postby crewzer on Sun Dec 04, 2005 2:17 pm

The new shunt arrived yesterday afternoon. So did the clouds, unfortunately. So, I installed the shunt and I'll try for some useful readings next Saturday.

In the meantime, here is some interesting data:

36 V array -> 12 V battery bank; numbers I recorded from my MX- and Mate display at ~Noon on November 25, 2005:

Vin 46.0 V
Iin 14.0 A

Vout 13.4 V
Iout 42.1 A

That's an indicated 644 W in and an indicated 564 W out, or 87.6% efficiency.

36 V array -> 24 V battery bank (temporarily rewired); numbers I recorded from my MX displays at ~Noon on December 3, 2005:

Vin 46 V
Iin 12.2 A

Vout 27.4 V
Iout 19.2 A

That's an indicated 561 W in and an indicated 526 W out, or 93.7% efficiency -- quite an improvement!
090805 System Configuration: 966 W STC (849 W CEC PTC) 48V PV array, FM80, 24V x 400 Ah AGM battery bank, FX2524T w/ BTS, Hub-4 & Mate; Link-10 w/ BTS, & E-Panel.
User avatar
crewzer
Forum Emperor
 
Posts: 1927
Joined: Mon Sep 27, 2004 10:50 am
Location: Vienna, VA

Postby crewzer on Wed Dec 07, 2005 4:21 pm

Following up... I was able to make some quick recordings and measurements today @ ~12:40 EST on my system (nominally 36 V in and 12 V out) with the new PV array shunt installed. Here's the data and calculations:

Indicated (on MX display):

Vin 47 V
Iin 13.2 A

Vout 14.6V
Iout 37.5 A

That’s an indicated 620.4 W in and an indicated 547.5 W out, or 88.2% efficiency.

Measured:

Vin 47.3 V (DVM measured across the MX-60 PV input)
Iin 12.5 A (DVM measured 12.5 mV across the 100mV / 100 A shunt)

Vout 14.62V (DVM measured across the the MX-60 output)
Iout 37.3 A (Link 10 indicated 37.1 A, plus 0.2 A for Link 10 consumption)

That’s a calculated 591.25 W in and an calculated 545.33 W out, or 92.2% efficiency -- that would be better, then! :grin:

The local weather forecast for this Saturday looks promising... I'll try again.

HTH,
Jim / crewzer
090805 System Configuration: 966 W STC (849 W CEC PTC) 48V PV array, FM80, 24V x 400 Ah AGM battery bank, FX2524T w/ BTS, Hub-4 & Mate; Link-10 w/ BTS, & E-Panel.
User avatar
crewzer
Forum Emperor
 
Posts: 1927
Joined: Mon Sep 27, 2004 10:50 am
Location: Vienna, VA

Postby crewzer on Sat Dec 10, 2005 10:03 am

Following up... I was able to make another set quick recordings and measurements today @ ~11:45 EST on my system (nominally 36 V in and 12 V out) with the new PV array shunt installed. Here's the data and calculations:

Indicated (on MX display):

Vin 48 V
Iin 13.0 A

Vout 13.8 V
Iout 39.6 A

That’s an indicated 624.0 W in and an indicated 546.5 W out, or 87.6% efficiency.

Measured:

Vin 48.4 V (DVM measured across the MX-60 PV input)
Iin 12.2 A (DVM measured 12.2 mV across the 100mV / 100 A shunt) -- cut & paste typo corrected -- thx, boB :oops:

Vout 13.8 (DVM measured across the the MX-60 output)
Iout 39.4 A (Link 10 indicated 39.2 A, plus 0.2 A for Link 10 consumption)

That’s a calculated 590.48 W in and an calculated 543.72 W out, or 92.1% efficiency -- that would be better, then! :cool:

It would seem that the "Amp in" calulation displayed on my MX' screen is consistently on the high side.

That's all, Folks!
Jim / crewzer :oops:
Last edited by crewzer on Sun Dec 11, 2005 2:43 am, edited 1 time in total.
090805 System Configuration: 966 W STC (849 W CEC PTC) 48V PV array, FM80, 24V x 400 Ah AGM battery bank, FX2524T w/ BTS, Hub-4 & Mate; Link-10 w/ BTS, & E-Panel.
User avatar
crewzer
Forum Emperor
 
Posts: 1927
Joined: Mon Sep 27, 2004 10:50 am
Location: Vienna, VA

Postby nsingh on Sat Dec 10, 2005 11:27 am

nsingh
Forum Expert
 
Posts: 74
Joined: Fri Dec 10, 2004 5:06 pm
Location: Mill Creek, WA

Postby crewzer on Sat Dec 10, 2005 1:44 pm