wire battery bank neg. post to ground bus?

Discussion about OutBack Inverters in Backup Applications

Moderators: OutBack Moderator Team, OutBack

wire battery bank neg. post to ground bus?

Postby Megunticook on Mon Dec 11, 2017 6:11 am

In my FP-Radian wiring diagram (http://www.outbackpower.com/downloads/documents/Make_the_Power/flexpower_radian/fpradian_qsg.pdf) it shows a green ground wire running from the battery bank to the EGC bus in the Load Center. Is this supposed to connect to the negative battery post, or does it just indicate that the battery enclosure itself should be grounded if it's metal?
User avatar
Megunticook
Forum Expert
 
Posts: 65
Joined: Fri Sep 29, 2017 4:08 am
Location: Maine
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH

Re: wire battery bank neg. post to ground bus?

Postby Mike Curran on Mon Dec 11, 2017 8:42 am

You got it, it's for a metal battery enclosure (does such a thing exist :???: ?). Definitely not to the negative battery terminal.
Mike Curran
Forum Guru
 
Posts: 463
Joined: Sat Aug 28, 2004 6:28 pm
Location: Chagrin Falls, Ohio
My RE system: Outback:
- 8 (2x4) Evergreen 180's into one MX60
- 6 (2×3) ALEO S79-300's into one FM80
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC
- 12 Surrette/Rolls 2V x 1766Ah
- Hub10.3, Mate3, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar:
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied.

Re: wire battery bank neg. post to ground bus?

Postby Megunticook on Mon Dec 11, 2017 8:51 am

Thanks, just wanted to be sure. I've spent a bit of time wiring vehicles, where you always make sure you have a 10 gauge wire from the negative battery post to the chassis in addition to the negative battery cable to the engine block. But a vehicle is obviously a different animal than a residential solar system, since the chassis itself serves the same role as the neutral wire in household systems, completing the circuits to the various loads.

Appreciate the help.

And yes, my battery box is wood, can't image why you would use metal instead.
User avatar
Megunticook
Forum Expert
 
Posts: 65
Joined: Fri Sep 29, 2017 4:08 am
Location: Maine
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH

Re: wire battery bank neg. post to ground bus?

Postby pss on Sat Jan 06, 2018 9:22 am

Regarding the metal battery enclosure, in my location in Southern California, state code regulations require batteries to be in metal boxes or on metal shelves, not wooden, with adequate ventilation if flooded lead acid. I simply used a strong metal shelving unit. Wood is not allowed due to risk of catching on fire. So, for those contemplating building a battery box out of wood, I'd say use aluminum fraework and maybe polyethelyene or other plastic walls.
pss
Forum Expert
 
Posts: 62
Joined: Mon Jul 24, 2017 8:40 am
My RE system: 7800 watts in three strings, Flexmax 60 x 3, Radian 8046A, GLSC load center, Mate 3, Hub 10.3 and 900 Amp, 48V Trojan T105-RE battery bank.

Re: wire battery bank neg. post to ground bus?

Postby raysun on Sat Jan 06, 2018 9:45 am

I use an Outback IBE3 for my battery enclosure. All metal construction.
raysun
Forum Expert
 
Posts: 54
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower One: FX3048T, MX80, MATE3s, FlexNetDC
Outback 200NC batteries (8 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 4Sx3P)