Post by Megunticook » Wed Dec 06, 2017 5:26 pm

Just getting ready to put my grid-tie with battery backup system in service (inspector coming Friday!).

I have 8 6 volt lead acid batteries wired in series (Rolls Surette S-550). I've wired them together and the cables to the inverter are wired at the inverter, but I held off on connecting those to the bank. I have some experience dealing with vehicle batteries but have never handled a bank with this kind of power. What's the safe procedure for making those final connections? With the battery breakers open, and a careful check inside the GSLC to make sure I didn't leave any tools inside or cross up any wiring, my plan was to connect the positive cables to the battery first, then connect the negative cables last. Will be wearing gloves and goggles. Is this the correct way to proceed?

And when disconnecting, always disconnect the negative first?

Thanks for any advice.
https://sunnypower.org

JRHill
Forum Czar
Posts: 876
Joined: Thu Feb 17, 2011 11:12 am

Re: safely connecting a battery bank

Post by JRHill » Wed Dec 06, 2017 10:55 pm

If you have to ask this question then you should probably hire a tradesman.

User avatar
Megunticook
Forum Guru
Posts: 242
Joined: Fri Sep 29, 2017 4:08 am
My RE system: 6.4 kW solar array (21 QCell 305 panels in strings of 3)
GS8048A FLEXpower Radian (Radian 8048A, 2 FlexMax 80 cc's, Mate 3s, FlexNet DC, Hub)
8x6v Rolls-Surette 550 FLA batteries, 428AH
Location: Maine
Contact:

Re: safely connecting a battery bank

Post by Megunticook » Thu Dec 07, 2017 7:36 am

Whether or not I hire a tradesman to make the initial connection, it's important for me to know how to properly connect and disconnect the battery bank because there may be situations down the road where that needs to be done and a tradesman is not available.

I probably should've hired a company to install my whole system (I did get proposals from several but because of availability issues and a looming net metering deadline, I ended up doing the entire install myself), but the process of learning how it's done and doing it has given me all kinds of important knowledge that will help me maintain everything well and keep things safe.

I respect the danger of electricity and am trying to educate myself on the safest methods to perform important tasks like disconnecting the battery bank.

So...back to the original question. Breakers open, positive cables first, then negative cables?
https://sunnypower.org

JRHill
Forum Czar
Posts: 876
Joined: Thu Feb 17, 2011 11:12 am

Re: safely connecting a battery bank

Post by JRHill » Thu Dec 07, 2017 9:18 am

Once the loads are shut down and the the breaker is opened, it the negative first, then the positive. Formally, it doesn't matter which cable is removed 1st on a negative ground system but depending on the enclosure or other metal items around, once the neg is removed there'll be no shorting hazard except between the battery terminals.

Mike Curran
Forum Emperor
Posts: 1658
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 (2x7) Talesun 275W (DC array input to SB charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input (manual switch during grid outage only) from 14 Talesun 275W,
Enphase M215 microinverters, normally direct grid tied

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: safely connecting a battery bank

Post by Mike Curran » Thu Dec 07, 2017 9:23 am

That's how I would do it. I installed my entire system myself also. As long as your battery->inverter breaker(s) are open you should be okay.

When I added more PV and an FM80 last year I powered down my system, opened the battery breakers and disconnected the positive cable at the battery, making sure it was secured away from the terminal before I started working inside the PSDC enclosure. FYI
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221

spirit
Forum Member
Posts: 7
Joined: Tue Dec 05, 2017 4:09 pm
My RE system: VFXR2812; FM80; Mate3s; Hub, PV 940W, FLA batteries 1,185Ah; grid-connected backup

Re: safely connecting a battery bank

Post by spirit » Mon Jan 22, 2018 3:04 pm

I'm not a professional installer, but I can tell you how I did this. I obtained a DC switch of sufficient amperage rating for my system from a marine supplier (an adequate DC breaker could probably also be used). I installed the DC switch (in the off or open position) in the positive line between my battery bank and inverter. Then, I made sure that the AC supply to the inverter was off and the AC load from the inverter was off (to make sure there was no supply to or load on the inverter). Then I first turned the DC switch to on, then turned on the AC supply to the inverter (breaker), then turned on the AC load from the inverter (breaker). Finally, I wrote up and printed the correct disconnect and connect sequence and posted that near my system. Disconnect: AC load, then AC supply, then DC. Connect: DC, then AC supply, then AC load. Hope this helps.

User avatar
tallgirl
Forum Emperor
Posts: 4334
Joined: Wed Sep 26, 2007 9:59 am
My RE system: 16 Kyocera KC175GT (2,800 watts DC), MX-60, 2 OutBack GVFX3648, 8 GC2 batteries (6v @ 215AH),
Location: Austin, TX

Re: safely connecting a battery bank

Post by tallgirl » Tue Jan 23, 2018 7:38 am

JRHill wrote:If you have to ask this question then you should probably hire a tradesman.
This needs to be pinned at the top of a LOT of forums.
Julie in Texas

I ride bicycles. A lot.