I am busy installing 2x VFX3048E Inverter/Chargers connected in parallel, ie 6kW 240VAC out. The system will run as a backup, ie critical loads will run via the inverter. "Passthrough"while utility/grid is available and off battery backup when utility/grid fails. I need clarity on the connection of the "Neutral" of the system. Can the inverter "Neutral Out" be connected to the utility/grid neutral?

Regards

Terrence
Terrence
Forum Junior Member
 
Posts: 1
Joined: Thu Feb 05, 2015 10:00 pm
My RE system: VFX3048E, MATE3, HUB10

Re: VFX3048E as backup system

Postby blackswan555 on Sat Feb 07, 2015 3:26 am

Neutral in and out are common / not switched,(Exept " M" series iirc) So you could to save cabling just run one common N back to the main bus