SimpliPhi 3.8 @ 48V - AH capacity

Post by raysun » Tue Jul 28, 2020 12:41 pm

The battery specification claims 75AH capacity (I suspect @ 100H) and 60A useable (80% DoD).

What have folks decided to use for capacity in the FNDC? How did you derive the figure?

User avatar
Greg T Fordan
OutBack Technical Service
Posts: 361
Joined: Fri Dec 29, 2017 1:56 pm
My RE system: Radian, FM80, FNDC, 48V batt bank

Re: SimpliPhi 3.8 @ 48V - AH capacity

Post by Greg T Fordan » Tue Jul 28, 2020 3:28 pm

Excerpt from an OB application note:
Simply.JPG
Greg T Fordan
EngTech
Outback Power Technologies

raysun
Forum Emperor
Posts: 2993
Joined: Tue Jul 26, 2016 5:57 am
My RE system: Flexpower Two: (2) FXR3048A, (2) FM80, MATE3s, FlexNetDC
SimpliPhi 48-3.8 (6 @ 48v)
Outback IBR3 battery enclosure
Suniva 330 watt panels (12 - 6 strings of 2 in series)
Hyundai 355 watt panels (6 - 3 strings of 2 in series)
Honda EU7000is gas fuel generator

Re: SimpliPhi 3.8 @ 48V - AH capacity

Post by raysun » Tue Jul 28, 2020 4:29 pm

Thanks Greg. We're working with 8 monoblocks.

SimpliPhi uses some fairly high rate for discharge metrics, and I'm trying to get a read on what folks found as practical capacity measure.

sodamo
Forum Czar
Posts: 843
Joined: Mon Apr 03, 2006 1:55 am
My RE system: Totally off grid - Hamakua side, Big Island, Hi

36 Trina 280 & 16 Phono 250 in 48 volt array (fixed) 14080w
Radians GG8048/GS4048 w GSLCs
4 FM 80 charge controllers
Hub 10.3
FNDC w/3 shunts
Mate 3s
OpticsRE - MMKL - Ninole Hi
12 SimpliPhi 3.8
14Kw Kohler 14RESA Propane

Charging Only
2FX3048T
Hub
FNDC. - shared shunt feeds from Radian FNDC
Mate 3s
10Kw MEP 803a Military gen

Honda EU7000i

Davis VantagePro2 Wx Station
On line at: https://www.wunderground.com/dashboard/pws/KHININOL2
Location: Ninole, Hi

Re: SimpliPhi 3.8 @ 48V - AH capacity

Post by sodamo » Wed Jul 29, 2020 1:40 am

This is my settings since Jan
12 @ 75 = 900

Hmmm, cannot post pic ](*,)
David
Please visit http://vacation.ninolehawaii.com

Mike Curran
Forum Emperor
Posts: 1804
Joined: Sat Aug 28, 2004 6:28 pm
My RE system: Outback - Garage roof:
- 8 (2x4) Evergreen 180's into one FM80 (2007/2020 - replaced MX60)
- 6 (2×3) ALEO S79-300's into one FM80 (2017)
- 2 grid-tied GVFX3524's classic stacked for 120/240VAC (2007)
- 12 Surrette/Rolls 2V x 1766Ah (2007)
- Hub10.3, Mate3s, FNDC, RTS, OpticsRE. Tigo Energy ES maximizers on each PV module.

Westinghouse Solar - Barn roof: (2012)
- 30 (2x15) 235W panels with Enphase M215 microinverters, grid-tied

Outback Skybox - Barn roof: (2019)
- 14 Talesun 275W in series (DC array input to SB inverter/charger)
- 3 SimpliPhi 3.8 batteries, 48V, 225Ah total
- AC coupled input (manual switch during grid outage only) from 14 Talesun 275W,
Enphase M215 microinverters, normally direct grid tied

All self-designed and self-installed
Location: Chagrin Falls, Ohio

Re: SimpliPhi 3.8 @ 48V - AH capacity

Post by Mike Curran » Wed Jul 29, 2020 5:39 am

3 @ 225Ah total:
Screenshot_20200729-083759_Samsung Internet.jpg
No FNDC with Skybox, however.
http://www.tigoenergy.com/site.php?95b2dca2-ca6c
https://enlighten.enphaseenergy.com/public/systems/Hctc107221